11/27/2021 7:51 PM | |
Joined: 12/18/2014 Last visit: 9/25/2024 Posts: 33837 Rating: (4205)
|
The LOGO! only knows Integer values. You can send via Profinet integer values. For real data you can use the special blocks F/I converter. For communication I would suggest, that the LOGO! is the client, S7-1200 is the slave. Look at this example application: LOGO! - S7 Connection with LOGO! Client and S7-1200/1500 Server |
This contribution was helpful to1 thankful Users |
11/29/2021 8:19 AM | |
Joined: 1/21/2021 Last visit: 5/31/2024 Posts: 2 Rating: (0) |
Hi ixo65, Thanks, this example was helpful. |