1/19/2021 4:21 PM | |
Joined: 3/14/2008 Last visit: 8/7/2024 Posts: 2080 Rating:
Hi, If you have two CS, you can use QCS:= 1 and QCS:=2 as start conditions. For enable in run, you need to set: ENASTART to 1 SELFCOMP to 0 CONT to 1(in auto mode) Then you can start a new sequencer. The SFC will go through STARTING directly to the prepared CS. Please be aware to use READY_TC:=0 in your starting conditions of the sequeners. |
Last edited by: Oreca at: 01/19/2021 16:25:46If I could help you, you can use the RATE button. Thank you. |
This contribution was helpful to
2 thankful Users |
1/19/2021 5:58 PM | |
Hi, See attachment.. You can configure the start conditions of the sequencer as seen on the left, and the rest like ENASTART, SELFCOMP, CONT are SFC parameters which you configure at the SFC instance. |
3 thankful Users |