2/27/2017 7:51 PM | |
Joined: 3/27/2009 Last visit: 7/17/2024 Posts: 92 Rating: (6) |
Send the program that you setup for the logo and the KTP400 HMI screen. So that we can see and advise. |
3/1/2017 11:09 AM | |
Joined: 11/16/2012 Last visit: 3/10/2024 Posts: 307 Rating: (52) |
On the HMI, you need a Word tag, e.g. VW10. This is required as a trigger tag. For each bit from this Word you can then create an alarm message. Note that the bit 0 from VB10 is the trigger bit 8 in VW10, and the bit 0 from VB11 is the trigger bit 0 from VW10. Assign these alarm messages to an alarm class, e.g. My_Alarm-Class. Create a screen with an alarm control that displays the messages of your alarm class. On the logo you then use network outputs for the alarm tags. Use the bytes VB10 and VB11 for this in this example.
AttachmentAlarm Tags.pdf (1318 Downloads) |
Last edited by: MicTsc at: 3/1/2017 11:12:33 AMLast edited by: MicTsc at: 3/1/2017 7:55:55 PM |
This contribution was helpful to7 thankful Users |
6/4/2019 2:21 PM | |
Joined: 7/6/2017 Last visit: 4/28/2024 Posts: 43 Rating: (2) |
Thank you |
This contribution was helpful to1 thankful Users |
6/4/2019 2:23 PM | |
Joined: 12/18/2014 Last visit: 8/7/2024 Posts: 33501 Rating: (4162)
Hello Luwarick, you're welcome.... |