I using EasyBuilder Pro V6.09.01.357 Build 2023.11.23. Thanks to distributor of weintek from multiprojekt.pl I have fixed drivers from weintek and in my opinion they works ok. For correct support of string in s7-1200 You have to set ascii variable as DBx_String1 and in drivers setting it shoud be set : Device Setting->Parameter Setting->Register Behavior->String Type-> No Fill. Then You can correctly display and input ascii string and there is no need for writing scripts in hmi. AttachmentDBn_String.zip (394 Downloads) |