2/13/2010 9:40 AM | |
Posts: 131 Rating: (0) |
Dear KSN. i actually have 2 free slots in my simadyn rack. but what i must do with my existing CS61 ? i need it to communicate with my Simovert A drive. |
2/13/2010 10:19 AM | |
Posts: 131 Rating: (0) |
So, Mr. KSN, u mean i will plug my SS52 inside the CS61 ? |
2/13/2010 11:14 AM | |
Joined: 8/25/2006 Last visit: 7/17/2024 Posts: 2207 Rating: (278) |
I mean that you don't need to do anything with CS61. You should insert SS52 into CS7, then insert CS7+SS52 into the free 2 slots in Simadyn D rack. Configure CS7 and SS52 in master programm. Configure required telegrams in the struc. Make configuration in ComProfibus, load it into SS52. Configure also your Simatic S7. Connect SS52 and S7. Here is manual of Simadyn D hardware. |
Last edited by: KSN at: 2/13/2010 11:17 AM |
|
2/13/2010 1:30 PM | |
Joined: 8/25/2006 Last visit: 7/17/2024 Posts: 2207 Rating: (278) |
Struc is not sold by Siemens now. It is a discontinued product. And how do you work with Simadyn D if you have no Struc? If you have project loaded into Simadyn D CPU (made with Struc), you may use Strucview to see the program. |