8/21/2012 3:32 AM | |
Posts: 17 Rating: (1) |
Dear Expert, AttachmentC:\Documents and Settings\shuping.cao\Desktop\s120 profinet issues.pdf (354 Downloads) |
8/21/2012 3:33 AM | |
Posts: 17 Rating: (1) |
attached sample created by me.
AttachmentC:\Documents and Settings\shuping.cao\Desktop\Pns120.zip (353 Downloads) |
8/22/2012 3:21 AM | |
Posts: 17 Rating: (1) |
Dear Mr. ChristophD, 1) I am clear for fist question, I have make a misunderstanding. 2) yes, the picture shot is copy from other sample, but problemare same with that, it can not find the address of hw config at STARTER . and for the telgraph, I change to telegraph 390, and add a drive into the project, define it's telegraph 111. but the problem same( can not save and compile at HW Confige in STEP 7) do we find some documentation about how to confige the S120 with SIMATIC S7-300 . thank you very much. Yeapoy AttachmentC:\Documents and Settings\shuping.cao\Desktop\Pns120.zip (183 Downloads) |
8/24/2012 8:08 AM | |
Joined: 5/12/2006 Last visit: 11/12/2024 Posts: 22446 Rating: (3029)
|
Hello, but when you have installed Step7 V5.5.2 and driveES 5.4 you should know that's this versions are not comptatible ! For Step7 V5.5 you need the DriveES V5.5. The next issue is that DriveES must installed before Starter is installed. In your case i think the PN DeviceOM of starter ist not installed correctly. And in your projects you have configure a CU320-2 PN V4.5, this Version is not available with a Starter Version < V4.3.x ! Regards Christoph AttachmentC:\Documents and Settings\ef3dac00\Desktop\compatibility_Chart_may12.pdf (246 Downloads) |
Last edited by: ChristophD at: 8/24/2012 8:12 AM |
|
5/9/2017 4:03 PM | |
Joined: 9/3/2014 Last visit: 3/13/2019 Posts: 4766 Rating: (122) |
New question published by kuet is split to a separate thread with the subject Communication between s7 315-2 PN/DP with S120 using Profinet, SF & BF fault. Best regards |
6/1/2017 8:39 AM | |
Posts: 9 Rating: (0) |
Dear experts; I have able to communicate between s7 315-2 PN/DP with S120 using Profinet. Now i am facing a Problem that is the CPU Showing MAINT LED. I have checked online diagnostic and found Maintenance Demanded. How can i solve this problem? My devices are …. CPU IP: 192.168.0.1. & CU320 IP : for X150 P1 is 192.168.0.15. Smart line module , double motor module and one servo motor. Please Check the attached file for better understand AttachmentScreen Shot.zip (173 Downloads) |