12/19/2023 12:01 PM | |
Joined: 8/3/2009 Last visit: 4/28/2025 Posts: 15368 Rating:
|
Hello Higorbm -> do not use the Auto setting in PGPC interface -> Use the TCPIP.1 setting also do you have installed SIMATIC Net PC Software on the WincC Prof RT PC? you need to because the communication driver comes with it. which PLC do you use? if you use a newer one with the Secure HMI communication check this: https://support.industry.siemens.com/cs/de/en/view/109803668 Also check the security level of your PLC and check in teh Tool Channel Diagnosis on your Runtime PC whats going on with your connection (send a Screenshot with the deteails) Bye Murof |
Last edited by: Murof at: 12/19/2023 12:02:11If this Information really helps, you could use the Rate function |
|