See the infeed module basic drawing . T. 72 is a NO contact of small relay. --if you checked all enabling and you all drives are no problem (drive status transfer back to infeed from device bus) --your yellow LED on ,your green LED off?--- if everything ok as you said it is possible that small relay has issue. I suggest --NOT replace control card for Infeed (it is not like drive--card and power section removable ) --you need replace the whole infeed module to trouble shooting --then send bad module to repair shop the infeed module version A,B or C will compatible if power rating same