4/26/2018 10:59 AM | |
Posts: 15 Rating: (0) |
Hi. Is it possibe to use a MP277 10" with the 425-2? We cent compile and get them to comunicate. Of course its in a hurry. :) |
4/26/2018 11:19 AM | |
Joined: 5/12/2006 Last visit: 5/2/2024 Posts: 22243 Rating: (2983) |
Hello, which SW do you use? Christoph |
4/26/2018 12:38 PM | |
Posts: 15 Rating: (0) |
We use the TIA 14 Yes, compilation error. |
4/26/2018 12:56 PM | |
Joined: 5/12/2006 Last visit: 5/2/2024 Posts: 22243 Rating: (2983)
|
Hi, and which compile error or is this a big secret? |
4/26/2018 1:20 PM | |
Posts: 15 Rating: (0) |
I will start the compile again so i can take a snap of the error. |
4/26/2018 1:25 PM | |
Posts: 15 Rating: (0) |
Here it is. |
4/26/2018 1:28 PM | |
Posts: 15 Rating: (0) |
|
4/26/2018 1:32 PM | |
Joined: 5/12/2006 Last visit: 5/2/2024 Posts: 22243 Rating: (2983)
|
Hello, wrong device version. Change the version of the Panel to V12 then the error should be solved.
Christoph |
4/26/2018 2:00 PM | |
Posts: 15 Rating: (0) |
Do you mean in the HW config? Or the sw in the HMI? We tested 12 in the HW config with the same result. |
4/26/2018 2:02 PM | |
Posts: 15 Rating: (0) |
We get this warning.. |