4/15/2019 3:43 PM | |
Joined: 11/21/2007 Last visit: 3/14/2024 Posts: 2323 Rating: (306) |
Hello Experts ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 4/16/2019 10:46:26 AMNew subject after splitting There is no such thing as the last bug in a program |
|
4/16/2019 11:01 AM | |
Joined: 10/11/2006 Last visit: 4/30/2024 Posts: 5827 Rating: (789)
|
Hello, if PM240-2 is required, please note, that specially the larger modules have braking choppers with limited capacity: https://support.industry.siemens.com/cs/ww/en/view/109760188 That can require a substantial oversizing! |
With best regards, |
|
This contribution was helpful to2 thankful Users |
4/17/2019 8:35 AM | |
Joined: 11/21/2007 Last visit: 3/14/2024 Posts: 2323 Rating: (306) |
This is what has been selected by our local contact : SIMOTION
D410-2 DP/PN
: 6AU1410-2AD00-0AA0
|
There is no such thing as the last bug in a program |
|
4/22/2019 8:55 PM | |
Joined: 3/9/2012 Last visit: 4/10/2024 Posts: 95 Rating: (8) |
The nominal power of the motor is 110kW and from the resistor 125kW. Normally you have a big power peak at cross cutters .So maybe this is not sufficient. To have more braking power, maybe a bigger power block has to be installed - or a 120kW ALM with 200A MoMo |