Dear all I start simotion D445, but finally 7segment of cpu remain in " 6" without dot, Stop and PN LEDs are blinking. What is the problem you think? See attachment file. Regards AttachmentVID-20220610-WA0000 (video-converter.com) (2).avi (546 Downloads) |
Last edited by: Brave boy at: 06/09/2022 22:23:50 |
|
6/10/2022 11:38 AM | |
Joined: 5/12/2006 Last visit: 11/14/2024 Posts: 22452 Rating: (3030)
|
maybe the project. i would rename the USER Folder on the card and check if the CPU boot up with only FW. |
6/10/2022 1:33 PM | |
Joined: 5/12/2006 Last visit: 11/14/2024 Posts: 22452 Rating: (3030)
|
yes on cf card leds this should be one Stop yellow and RDY green blinking |
6/11/2022 10:36 AM | |
Joined: 9/2/2020 Last visit: 11/14/2024 Posts: 60 Rating: (0) |
Hi I put mode selector on 3 and power on cpu again. Now 7 segment is 6, Run Led is on and green (continues) and Rdy Led is green blinking (see attachment). Apparently cpu is run but machine doesn't work. Regards AttachmentVID-20220611-WA0012 (video-converter.com) (1).mpg (575 Downloads) |
Last edited by: Brave boy at: 06/11/2022 11:39:57 |
|
6/11/2022 7:14 PM | |
Joined: 5/12/2006 Last visit: 11/14/2024 Posts: 22452 Rating: (3030)
|
with mode 3 you delete all data, so please open the project and down,load it again (after switch back to mode 0) |