5/20/2022 11:10 AM | |
Joined: 3/11/2019 Last visit: 8/7/2024 Posts: 1545 Rating: (277) |
Hi Makronaut, it is not possible as PLCSIM does not support fieldbus systems with real hardware components. If you need a software based solution, there are "real software plc's", but PLCSIM is only a simulation. S7-PLCSIMH systems are not supported by S7-PLCSIM.PROFINET I/O is not supported by PLCSIMregards sancruz |
Feedback appreciated, please rate |
|
5/20/2022 11:41 AM | |
Joined: 7/9/2015 Last visit: 8/7/2024 Posts: 3915 Rating: (577)
|
Hi, what about Proneta? Check this: PRONETA Basic 3.3 Commissioning and Diagnostics Tool for PROFINETRegards, Towome |
|
|
This contribution was helpful to1 thankful Users |