Hello, Can you please describe a little bit more about the status when it "doesn't work"? Is there a link between connected participants (Port LEDs)? Did you also try to use the fiber optic connection over XCM-102 with "normal" Ethernet Components, like PC with pinging other end connected PC? Are there any errors, alarms present in SIMOTION and/or DCM (also Diagnostic buffer)? If you are using IRT communication you should adjust delay time on refering topology connection, because in manual of XCM102 there is a statement about throughput times of max. 1,760µs. https://support.industry.siemens.com/cs/ww/en/view/109962970(chap.3.2) Default value is 0,6µs for up to 100m copper cable. So, it have to be changed to ~1,8µs plus length of copper cables from SIMOTION to XCM102and from 2nd XCM102to DCM CBE20. |