Joined: 4/23/2010 Last visit: 12/31/2023 Posts: 8092 Rating: (877) |
Hello, A0503 = Under voltage limit, Main supply failed & subsequently DC bus voltage is below limit. F01601 = system start up error. For this check value in r0949. The fault code will help you to identify the cause of fault. Please refer the attached sheet for r0949 fault code values. AttachmentG120_F01601 r0949 fault codes.pdf (447 Downloads) |