Hello, The following text is part of an instruction manual for Sinumerik: "The Smart Line Module (5/10kW) is controlled using the -X21, -X22 terminal block. A control of the line contactor by the Smart Line Module or in conjunction with the Control Unit is not provided. If, however, a line contactor is used, it must be switched with a PLC or hardware control, for example. See also Section Safety Integrated and Section Line Contactor Control. If the Smart Line Module has been switched on, the DC link has been precharged and no faults are present, the unit uses the "Ready" digital output to signal the "infeed ready" status. This signal must then be fed appropriately to the Control Unit using an external interconnection. |