6/29/2015 12:01 PM | |
Posts: 26 Rating:
|
I believe that unlike MM you cant do it on SV20. For 4 to 20 mA you have to apply deadband and scale it properly. See manual for P0761 (relevant pages in attachment) There is an explenation for this parameter which shows you steps to produce 2 - 10 V analog input. The very same way you can change it for analog output 4 to 20mA or whatever you want. You just adapt P0770 which is x1 of analog output scaling instead of P0757 (x1 of AI) Instead of P0760 (y2 of AI) change P0780 (y2 of AO), instead of P0758 change P0778 (y1 of AO) Instead of P0759 (x2 of AI) you change P0779 (x2 of AO) Instead of P0761 (deadband of AI) you set P0781 (deadband of AO)
AttachmentV20_Analog_IN_OUT.pdf (1015 Downloads) |
This contribution was helpful to
1 thankful Users |
7/6/2015 9:57 AM | |
Posts: 26 Rating:
|
Well you could always put some resistance (500 mΏ) and therefore achieve voltage output of 0-10V instead of 0-20mA, but it stil wouldn't energize your ssr. |
Follow us on