Hello Nicer,Attached please find the part of our manual describing the values from the sensor cell through the pressure transducer block into the appropriate output values.The picture under 7.1.3 explains the differences between the values. At the first glance a scaling for PROFIBUS PA does not make any sense. Especially if you are measuring pressure and forward the pressure value to the control system. For a flow measurement this will be a different issue. The pressure value will be changed to 0…1 (0…100%). This value can be transformed into the flow value (dependence see attachment in my previous information). The working range can finally change the value to a flow unit.