HI Dears I have a question,How can I have software redundancy in cpu 315-2dp?Please guide me thanks zmzm |
11/7/2010 10:48 AM | |
Joined: 7/2/2008 Last visit: 11/27/2023 Posts: 928 Rating:
|
Hello zmzm, It's not that easy to tell you ina single post how to do it. I recommend that you should 1st read the manual very carefully. Briefly, 1- You can use the MPI interface to build a redundant link over MPI (you can read on how to do it in manual) 2- You can use the integrated DP master of the CPU to communicate with ET200Ms. The ET200Ms should come in RED. Bundles. 3- You can use the MPI link for OP communication but I don't recommend it. 4- You can use Ethernet CPs for OP communication. If you tell me more about your application I can guide you more. Best regards. H-H |