on whatrate exchange CPU317 and CP341 to the bus (K-bus)? |
10/5/2010 6:52 PM | |
Posts: 8946 Rating:
|
187.5 kBit |
10/6/2010 10:24 AM | |
Joined: 10/7/2005 Last visit: 11/28/2023 Posts: 2996 Rating:
|
Hello gre_m don't worry too much about the "slow" K-bus speed in an S7-300. While it usedfro some communicationsbetween the CPU and CP's, the user data that you read from the CP is actually transfered via the the fast I/O related P-Bus (you'll notice that any CP in an S7-300 occupies 16 bytes of I/O space which is used for this purpose). I hope this helps |
Cheers |
|