Hi All I am Working on S7 400H ( CPU 412-5h ) Having Error of 16# 43E7. I have Already Changed m CPU and MMC Card But Still Problem Exist. Kindly Request you all to Help me to get out of this. Also I am Submitting Text file of Dignose for more infos. Event 1 of 120: Event ID 16# 43E7 Standby CPU: Link-up/update by master CPU aborted Cause: LINK-UP aborted due to active test and startup or object management function Previous operating mode: STOP (internal) Requested operating mode: STOP (internal) Event occurred in the standby CPU in rack 1 Incoming event 08:01:05.746 PM 01/01/1994 (Coding: 16# 43E7 F144 0050 43DD 0000 0000)
AttachmentDiagnose.txt (537 Downloads) |
10/6/2023 8:39 AM | |
Joined: 5/6/2022 Last visit: 11/8/2024 Posts: 489 Rating: (98) |
Hi SS69283, This error may be due to the synchronization modules, where the fiber cables that connect both CPUs go, and which are surely defective. I would recommend checking the status LEDs of the synchronization modules on the CPU in rack 1.
|
If this Information really helps, you could use the Rate function |
|
11/2/2023 9:11 AM | |
Joined: 10/4/2020 Last visit: 11/8/2024 Posts: 21 Rating: (0) |
Issue Resolved ....Actually H sync Modules were faulty. |