7/21/2007 4:58 PM | |
Posts: 191 Rating: (58) |
Hi!! ¿ does it needs to be profibus ?? there is a very simple wayusing USS protocol try http://www.hmkdirect.com/siemens/Manual/MC_Manuals/1.5%20Chap%208.1%20USS.pdf Siemens sells a library for USS.. also try using the search engine of the forum asking for USS... good luck! ROSA |
7/23/2007 8:11 AM | |
Posts: 2930 Rating: (432) |
Hi SOON, to control drives like MM4x via Profibus you need a profibus master. The EM277 is a Probus Slave no a master. There is no Profbus master avaliable for the S7-200. If you want then you use gateways like ( www.anybus.com ) Use the USS protocoll. With USS-Protocol you can control up to 31 drives. Have a look to this URL. Here you can find more information. please note there are several examples how to use the USS-protocol. http://support.automation.siemens.com/WW/view/de/21690362 You can also find information in the S7-200 system manual at chapter 11. I hope this helps. Regards Helmut |
7/24/2007 9:20 AM | |
Posts: 2930 Rating: (432) |
Hi Soon, you can not use the profibus possibility with the S7-200 because for the S7-200 there is no profibus Master avaliable! You can use gateways ( www.anybus.com ) but this is a seperate HW and not from Siemens. USS is the only possibility S7-200 offers if you need to communicate via network to drives. Have a look to the S7-200 system manual. At chapter 11 you will find more informations. I hope this helps. Regards Helmut |
7/24/2007 9:48 AM | |
Joined: 10/5/2005 Last visit: 4/9/2024 Posts: 63 Rating: (6)
|
Hi Soon! Have a look to:
Regards, the Mausus |