6/27/2020 1:54 PM | |
Joined: 12/21/2019 Last visit: 10/8/2021 Posts: 12 Rating:
Dear All, We have used Simatic manager software V5.6 for S7-300 CPU 319-3 PN/DP with ET 200SP RIOs, During the testing with Modbus_Master programming , we found status error 8186, regarding MA_ ADDR Error of Slave Number is above if assigned 100, 101,102,103....... (Like 3 Digits). Please find the attached Screen short for your reference. Best & Regarding, Varadharajan. S ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 06/29/2020 10:25:08New subject after splitting |
6/28/2020 4:40 AM | |
Joined: 10/7/2005 Last visit: 7/14/2024 Posts: 3009 Rating:
Your screendump shows an MB_ADDR of W#16#100 which is a hexadecimal value that equates to 256 as a decimal Modbus Slave address. Valid ranges for Modbus slaves are 1 to 247 (decimal) in normal mode and 1 to 65535 (decimal) in extended address area mode (see also previously linked manual). Question is which mode are you using? |
Cheers |