9/26/2012 9:52 AM | |
Joined: 10/7/2005 Last visit: 10/17/2024 Posts: 3024 Rating: (1054)
|
Hello Arturas A Timer needs to "see" a change of state of the RLO to start. Your Timer though doesn't have a chance to see this change of state as you don't call the T4 related logic when DBX0.5 is0 (i.e. T4 never registers that the RLO was zero as it no longer being called). To fix this, put the T4 related logic somewhere were T4 is always being called. Be mindfultoo that RLO dependant Jump instructions (e.g.JC, JCN) themselves set the RLO to 1 (see <F1> context sensitive help on them) I hope this helps |
Cheers |
|
This contribution was helpful to1 thankful Users |
9/26/2012 11:43 AM | |
Joined: 1/27/2009 Last visit: 9/17/2024 Posts: 172 Rating: (8) |
Hello fritz, Thank you, code fixed. |
The only thing necessary for the triumph of evil is for good men to do nothing |
|
This contribution was helpful to1 thankful Users |