Hi Dimbas, I recomend to take out the synchronisation moduls and put them directly back, theReserve will go in STOP but the Master will saty in RUN. When the temperature is some higher and the sync-modules are not good in the slot then you get this kind of trouble. There is nothing defect but the modules are not placed properly, you may simulate this by briefly/kindly ticking with for example a screwdriver on the module. If it is this then the H-System will STOP the Reserve with the same error message you have mentioned. Please alsoupdate the CPUsthe Firmware to V3.1.4, you may search on the homepage and find the newest firmware, see the Attachement with version V3.1.4 mentioned, under ID 6741018 you can download the firmware. Attachment6741018 Operating System Updates for CPU414-4H - CPU417-4H.pdf (983 Downloads) |
I hope that the answer will help, if you have still questions, don't hesitate to ask me. |
|