Dear All. Please find following problem related to TDC in Steel Rolling Mill During normal operation, suddenly process mainly the data transfer from level 2 (setup) will be delayed by 12 to 15 second and slab oscillate before the stand for setup, after few second its become okay and rolling starts.After this problem we are not able to go online with any of the TDC CPU (4Nos) of speed masters through the development station and errors occurs is “ Cannot open the MPI interface”By the same development station we are able to go online with other TDC, we tried to restart the development station but in vain. We reset the TDC and it become okay. This is happing at the frequecncy of @twicein a month.Please let me know if somebody face thess type of problem and what is the cause behind the same. AttachmentTDC.zip (286 Downloads) |
12/30/2012 7:51 AM | |
Posts: 14 Rating: (0) |
Thanks for immediate reply I'll check and let you know. |
2/13/2014 10:58 AM | |
Joined: 8/25/2006 Last visit: 10/4/2024 Posts: 2209 Rating: (279)
|
Hello. Service utility always take additional load. You can read about this inSIMATIC TDC System- and communication configuring D7-SYS, chapter 3.13.2 'System load, response times'. Try to reduce the load of all CPU's of the problem rack. Try to use separate CP51M1 (separate network) for service purposes. Check all cables, switches, other network components.
|