4/8/2014 4:51 PM | |
Posts: 9 Rating: (0) |
Hi, i have some problem with analog module, i attachment de pictures of the problem. I am occupying a type J thermocouple, and i read a bad temperature. I read that in this module i do not need scaling with FC105, only connect, configure and read in °C. But with 20°[C] room temperature read in PIW 514 -58. i changed thermocouple position and i have the same problem. Please, anybody help me?.
AttachmentProblem.zip (406 Downloads) |
4/8/2014 5:17 PM | |
Joined: 4/22/2010 Last visit: 10/17/2024 Posts: 5697 Rating: (715)
|
Hello, Please have a look at the S7-400 module Data manual, to setup and connect your card. If stiil problems, please return and tell us about your settings and connections. Regards, Marcjan |
Problem solved? |
|
4/9/2014 3:48 AM | |
Posts: 9 Rating: (0) |
still i have problems. The Measuring range module settings is A. |
4/9/2014 8:07 PM | |
Posts: 9 Rating: (0) |
i am not usingcompensation method. Maybe these is a problem. I dont know how use it. |
4/10/2014 3:57 AM | |
Posts: 9 Rating: (0) |
I tried connecting a PT100 to channel 0, and connected thermocouple to channel 2. I get the status value 32767.
Attachment2.zip (380 Downloads) |
4/10/2014 8:08 AM | |
Joined: 4/22/2010 Last visit: 10/17/2024 Posts: 5697 Rating: (715)
|
Hello, First of all i see no wires going to L+ and M to supply the card. The PT100 must be conected to channel 0 and 1 (4 wire) If you have 2 wire sensor you must bridge 6 to 11 and 7 to 12. See attached document. Regards, Marcjan Attachmentwiring1KF10.pdf (436 Downloads) |
Problem solved? |
|
4/10/2014 12:44 PM | |
Posts: 2348 Rating: (264)
|
Agree, first of all you should make RTD sensor work. L+ and M required of course. |