9/9/2016 8:01 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1051) |
hi, in fact it is a new device the firmware is V4.1 6ES7214-1AG40-0XB0What kind of TIA-Version do you have? latest is V13 SP1 Upd9 As you can see in the technical data, the CPU with FW4.1 is projectable since V13 SP1. If you have not installed the relavant updates, use the TIA-updater or follow this link to download it: Service Pack 1 for SIMATIC STEP 7 V13 incl. PLCSIM (TIA Portal)Updates for STEP 7 V13 SP1 and WinCC V13 SP1hope this helps, regards, |
FCK WAR! |
|
This contribution was helpful to1 thankful Users |
9/9/2016 8:23 AM | |
Joined: 5/12/2006 Last visit: 6/3/2024 Posts: 22254 Rating: (2986)
|
Hi, sorry but this is not right! The PLC is first released with FW V4,0, so it can be that is now FW V4.1 but the initial Release was FW V4.0 (https://support.industry.siemens.com/cs/ww/en/view/86567043) From the Screen we see that the PLC type is identified corrctly so the TIA Portal Version should not be the Problem. Regards |
This contribution was helpful to1 thankful Users |
9/9/2016 9:00 AM | |
Joined: 3/5/2014 Last visit: 8/5/2022 Posts: 5521 Rating: (1051) |
hi Christoph, thanks for the hint. isn´t it possible that the projected CPU has a FW-version 4.0 with V13 without SP and he can find the newer CPU with FW 4.1 but is not able to load it? My thougth were that he surely had tried al available FW-versions in TIA, and FW4.1 is only available since SP1, so maybe the SW is not up to date. regards, |
FCK WAR! |
|