1/8/2024 7:50 PM | |
Joined: 9/21/2012 Last visit: 11/18/2024 Posts: 4199 Rating: (474) |
Is this behaviour with HMI simulation or with a real HMI? |
1/8/2024 7:53 PM | |
Joined: 10/14/2018 Last visit: 10/15/2024 Posts: 3 Rating: (0) |
real HMI, real PLC, Tomorrow can make a video |
1/9/2024 6:41 PM | |
Joined: 10/14/2018 Last visit: 10/15/2024 Posts: 3 Rating: (0) |
Dear experts, thank you for suggestions. The IW0 was used as a return value of RD_SYS_T (read system time) and of course IB0 IB1 was used for standard DIs in HW cfg. PLC program looked like copy/paste from diff project so I had to edit a lot of things. After everything its working as expected even in TIA16. So I think I found WHY its happening, but did not even expect the fault like this. The problem there was always false bit used as IN/OUT of FC doing program stepper. I hope I dont dissapoint you, but it happends while company programmer dont know what is doing. We will never ask that company for any contract. Once again experts, Thank you for your time! |
Last edited by: Jen_Moderator at: 01/10/2024 09:10:27Video embedded. |
|
This contribution was helpful to1 thankful Users |
Follow us on