Joined: 1/21/2013 Last visit: 10/23/2024 Posts: 4620 Rating: (708) |
Hi YogendraG For the position no.1 You can find it in the manual Product data sheet 6ES7407-0KR02-0AA0 - Siemens Rated value at 230 V AC 0.5 A Volt-amps (VA) to amps (A) conversion calculator - RapidTables.comAmps to volt-amps (VA) conversion calculator - RapidTables.com |
Last edited by: Ste39 at: 4/4/2014 10:26 AM |
|
4/5/2014 9:13 AM | |
Joined: 1/21/2013 Last visit: 10/23/2024 Posts: 4620 Rating: (708) |
Hi YogendraG, For the power consumption of the module have a look: Calculating power consumption for PLC I/O signal module and power consumption from back Bus by DI module and How to claculate the power consumption and Power Consumption Regarding the calculation of consumption, if you calculate everything in VA example: 1500VA/230V = 6.5 A, so you'll need a transformer 2000VA calculating a bit of reserve. If you always such a transformer 1500VA but 110V will do 1500VA/110V = 13.63 A, but will always be a 2000VA transformer. And have a look our friend PISCEAN 2010 and DILIP 1111: Transformer Selection |
This contribution was helpful to1 thankful Users |
5/23/2014 7:08 PM | |
Posts: 559 Rating: (87) |
Dear YogendraG, For Control you can use tranformer from 500VA to 1 KVA. Also for power supply you can use 10A to 40 A power supply as per your requirement. Always go for 1.5 times higher rating then the actual load. |