4/23/2016 9:03 AM | |
Joined: 3/14/2008 Last visit: 5/7/2024 Posts: 2066 Rating: (928) |
Hi, I think you have compiled the OS and such. To which block did you connect the SelFp1 parameter? Is it a standard siemens APL block? Also, is the block with the SelFP1 also a standard Siemens APL block? You can try to use the "apdiag.exe" tool. Its a handy tool listed under C:\Program Files (x86)\SIEMENS\WINCC\uTools . You can open this in runtime and selecting "Output Window" and report back the diagnose when you click on the button. |
If I could help you, you can use the RATE button. Thank you. |
|
4/25/2016 5:26 PM | |
Joined: 3/14/2008 Last visit: 5/7/2024 Posts: 2066 Rating: (928) |
Hi CKO, You can check if OCM option is checked for the CFC block "Intlock8". It means that Operator Control and Monitoring parameters are compiled to the OS system. If that option is not checked, it could be possible that nothing happens when clicking on the faceplate. PS: If CKO uses a "Intlock8", it doesn't mean it is used as a Interlock (or protect or permit). But RugbyGuy is right when you do use this as your Interlock, then it should be connect to Interlock, because it's a APL functionality.
|
If I could help you, you can use the RATE button. Thank you. |
|