Salut Jacques_Maurice; Use the "Assign address" function in PDM. This FAQ will give you information on the physical requirements: When is it possible to change a field device address? |
Last edited by: dchartier at: 2/23/2013 3:03 PM |
|
2/23/2013 3:50 PM | |
Posts: 14 Rating: (0) |
thank you so much Daniel ! |
2/27/2013 1:54 AM | |
Joined: 6/13/2006 Last visit: 9/21/2023 Posts: 201 Rating: (8)
|
Hi, See the attached for hardware setup and the below settings for your PG. Setting of the properties- CP5611( profibus) tick the PG/PC is the only master on the bus timeout: 10s Transmission rate: 45.45kbps Hishest station address 126 Profile: DP Regards, chook AttachmentProfibus PA.pdf (216 Downloads) |
[IMG]http://i17.tinypic.com/66b7jas.jpg[/IMG] |
|
2/27/2013 2:05 AM | |
Joined: 9/27/2006 Last visit: 7/31/2024 Posts: 12272 Rating: (2676) |
Hello Jacques_Maurice; Chook's post explains the settings required to use PDM as a Class 2 master on a Profibus-DP network, when you are using DP/PA couplers. With a DP/PA link you would not have to miti the transmission speed to 45,45 lB. What you are trying to do, connecting PDM through Ethernet to the PLC, then switching to Profibus-DP and the Profibus-PA, is called "routing". Routing requires specific hardware in the programming PC and the PLC: What are the requirements for using SIMATIC PDM Data Record Routing?
|
2/27/2013 7:11 AM | |
Posts: 23 Rating: (5) |
hello Jacques please find the attachment. it may help you. |
Last edited by: O_Moderator at: 2/27/2013 7:47 AM |
|
This contribution was helpful to1 thankful Users |