8/29/2020 4:22 PM | |
Joined: 9/27/2006 Last visit: 5/7/2024 Posts: 12257 Rating: (2666) |
Hello Victor; As qwazee stated, the question is which type of range do you need for your project. You can use Norm_X alone, or in combination with Scale_x, or create your own function to scale your analog input. Norm_X will read your numerical value from the analog input channel and transform it to a REAL value in a normalized range of 0.0-1.0, or 0.0-100.0 (percentage), for example. Scale_X will take that normalized value and change the range (and adapt the value) to something you need in your project, for example 3.0-15.0 psi, or 20.0-2000.0 gpm... See this explanation of Norm_X from the TIA Portal v16 System manual: https://support.industry.siemens.com/cs/ww/en/view/109773506/93910599179 Hope this helps, |
Last edited by: dchartier at: 08/29/2020 16:28:07 |
|
8/29/2020 4:33 PM | |
Joined: 6/24/2013 Last visit: 5/2/2024 Posts: 1596 Rating: (410)
|
Hi I use my own block based on SCALE FC which covers for 1. out of range indication + alarm 2. bipolar/unipolar signals 3. 1..5V/4..20mA - also it does ignore (allowed by 4..20mA standard) small negative values on raw value 4. temperature measurement where analogue raw value is in degrees x 10 Printout attached AttachmentSCALE.pdf (450 Downloads) |
This contribution was helpful to1 thankful Users |