Joined: 1/21/2013 Last visit: 10/18/2024 Posts: 4620 Rating: (708) |
Hello, please check this post "Aminadra user": and http://support.automation.siemens.com/WW/view/en/24561702 2) Bus terminationIn contrast to MICROMASTER 4, the G110 / G120 (CU240x) / G120 (CU2x0x-2) have a built in bus termination and biasing facility. The correspondent bus termination DIP switches must be ON when the G110/G120 inverter is the last node on the RS485 bus. External resistors do not have to be connected. Therefor see also FAQ with Entry-ID:12462284
|
||||||||||||||||||
Last edited by: Ste39 at: 07/18/2019 17:15:32Last edited by: Ste39 at: 07/18/2019 17:37:46Last edited by: Ste39 at: 07/18/2019 17:39:00Last edited by: Jen_Moderator at: 07/19/2019 10:27:02Optimized link. |
|||||||||||||||||||