Hello together, in the operation instructions of V90, https://support.industry.siemens.com/cs/ww/en/view/109793501, page 206 you can see that the telegram 111 has one user defined WORD. On page 209, you can find the important info that with p29151 = 3: DI status, the status of the digital inputs is sent via this user defined WORD. I think that this would solve your issue, but you need to use the EPOS (basic positioner) in the V90 and telegram 111 for that. |