5/16/2017 8:40 AM | |
Joined: 3/14/2008 Last visit: 10/8/2024 Posts: 2109 Rating: (941)
|
Hi, Just compare the tank level with the parameter, if tank level is lower than parameter, then run a TimerP with mode=2 (on delay). If time expired, set Protect of the MotL to "0". The motor must be reset in order to start again. If you use Intlock, then the motor is started as soon as Intlock = 1 again. In think this is the easiest. Technological blocks feature External messages such as ExtMsg1,2,etc. You can also connect the timer to ExtMsg1 to create a message that the motor is stopped due the tank level. |
If I could help you, you can use the RATE button. Thank you. |
|