Hi GauravJoshi1989, I think this is because you have disabled your monitoring time for the valve and motor of the valve-> V_Monitor and M_Monitor. If the monitoring parameter is set to "0", the valve will wait with setting the feedback signal until the V_MonTiStatic (for valve) and M_MonTiStatic (for motor of valve) is elapsed. Could you try to enable V_Monitor and M_Monitor? If not, try to set the output commands: Open and Close to resp. FbkOpen and FbkClose. Or use: "NoFbkOpen" and "NoFbkClose" commands. I think this is an issue with the monitoring time...not with faceplate (assuming it is not changed). |