Joined: 7/10/2017 Last visit: 6/23/2024 Posts: 117 Rating: (2) |
Dear All, I am going to commission some Weighing Scales connected to Measuring/Display Unit BTW-100 (Bikotronic Digital Balance Unit), with S7-315 and Analog Ai8 x 13 BIT (6es7331-1kf02-0ab0).... BTW - 100: Reads Load Cell and Displays weight in Kgs.......It also gives an Analog Output (which according to Manual) 0-10V= or 2-10V=......................... Imax = 4mA, Rmax= 2.5kohm....... I am going to use this Analog Output with Ai8 module in S7.... This scale is connected to a SKIP which is dosed with Aggregate (of 3 different sizes) and taken up to Mixer.... Scale is fixed at the bottom and SKIP rests on it...... Dosing gates are just above SKIP and fills the SKIP for required size of Aggregate..... I measured the Output Analog Voltages as follows : Pin 1(-), Pin 2(+) SKIP on the Scale & Empty: Reads (-57 Kgs) and Voltage measured is (-1.3mV) SKIP on the Scale & FULL :Reads (+2335 Kgs.) and Voltage measured is (+7.87 V) SKIP on TOP & Scale FREE :Reads (-876 Kgs.) and Voltage measured is (-1.3 mV) I want to show this measured Value on my HMI....Though Negative Values need not to be shown and may be fixed to 0 Kgs. on HMI i.e All Negative values will be seen as 0 Kgs..... I am confused to use Measuring Range as +/-10V OR 0....10V also in FC105 what would be my High and Low Limit ? Also, what if Negative Voltage gives Error (Under Range/Under Flow) ? Thanks... Mr Ansari ------------------------------------------------------------------------------------------ |