Hi, I am have the problem with my webserver.
I have the CPU1214C 6ES7 214-1AE30-0XB0 V2.2.0 with TIA PORTAL V13 UPD5 When I clickHomepage of the applicationin the webserver amessage showed:AWP: Application Not Available : offline What is the problem? TIA Portal V13 is compatible with firmware V2.2.0? Thanks Cassio. |
11/6/2014 4:46 PM | |
Joined: 7/7/2010 Last visit: 10/14/2024 Posts: 15302 Rating: (2427)
|
From this post I read it as follows: You successfully went online via web browser to the default web server pages of the PLC. You created custom user defined web page(s) in the PLC project. You configured the hardware settings for the web server to point to the user defined pages. You clicked generate blocks to create the DBs required for your custom pages to work. You added a www instruction block to OB1 or something that runs every scan and put the proper DB #, like 333. You also downloaded your hardware configuration and started the plc, and now you cannot get online with your custom pages. Is all this correct? |
science guy |
|
This contribution was helpful to1 thankful Users |
11/7/2014 1:18 AM | |
Posts: 2 Rating: (0) |
From this post I read it as follows: You successfully went online via web browser to the default web server pages of the PLC. You created custom user defined web page(s) in the PLC project. You configured the hardware settings for the web server to point to the user defined pages. You clicked generate blocks to create the DBs required for your custom pages to work. You added a www instruction block to OB1 or something that runs every scan and put the proper DB #, like 333. You also downloaded your hardware configuration and started the plc, and now you cannot get online with your custom pages. Is all this correct? Hi,
I fix it. The problem was the instruction www. I declared CRTL_DB wrong. After this, onother messagem was displayed AWP: Application Not Available : initializing applicationI solved this problem switching the power off to the PLC. The PLC must have been stuck in some internal state that was then cleared after a full reboot. Thanks for help me. Cassio |