4/25/2012 3:09 PM | |
Joined: 12/20/2008 Last visit: 7/15/2024 Posts: 556 Rating: (236) |
I went throughthis. |
4/25/2012 3:27 PM | |
Posts: 8946 Rating: (999) |
No, loadcell is not included. |
4/25/2012 3:32 PM | |
Joined: 4/19/2008 Last visit: 6/25/2024 Posts: 1525 Rating: (159) |
Hello RajKiran, Siwarex is Only Module, Basically from Load Cell you will Get the mV Signal Which is get Sense by the Siwarex Module, You need to by Saperatly the Load Cell, Normally its Depends on the Machenical Constuction, Because there are so many type of Load Cell are there, Also you want Junction Box, where From All (Say for One Weighing Hopper 1, 2, 3 or 4 Load cell used ) you have to Bring to JB & then Only one Group of Cable is goes to Siwarex Module, Load Cell Having 4 Wire or 6 Wire Configuration, Here is the link for Calibration, But you will find Basic Diagarm for the Configuration. Calibrating SIWAREX U with SIWATOOL U Now it is Clear For You. |
Ammy |
|
This contribution was helpful to4 thankful Users |
4/25/2012 7:34 PM | |
Joined: 5/28/2008 Last visit: 7/17/2024 Posts: 4511 Rating: (838)
|
Hello, Just a small addition to my friends here. There are three ways to measure weighing signals from load cells:
What I wanted to highlight, choose the suitable module in according to your application. Hope this helps.
|
Ayman Elotaify |
|