Hello Raman S, Do you want to change SAFE POS LIMIT value or restart axis tripped/disabled due to safe position limit triggered alarm? If you want to change safe position limit, you can change values directly in MD. To restart axis when safe pos limit is operated, you need to follow below procedure/steps. For axis having absolute measuring system User agreement must be withdrawn i.e. all safety axes are listed in HMI display "user agreement" for which safe limit position or safe cams are activated. These are displayed as Machine name, SI position, User agreement. The User agreement status is either YES or NO. User need to set NO, so axis safe limit position will be disable, then in JOG can move axis to away from safe limit position & again user can activate User agreement. Please note user must use key at position 3 to deactivate & reactivate User agreement & its user responsibility to check axis SI position. OR if your axes has incremental measuring system, switch OFF & ON power of machine, move the axis in safe zone, reference it. After referencing check axis SI position on HMI. Hope this helps. |