11/15/2021 3:39 PM | |
Joined: 10/3/2021 Last visit: 6/5/2022 Posts: 1 Rating: (0) |
Hi everyone, I've got the problem when using SFB 15. I sent data from address "MD3" of PLC1 to address "MD3" of PLC2 and it worked but when I changed address"MD3" into "MD124" of PLC1; PLC2 didn't receive the data. And I got error #0 and status # 0019. Hope that Everyone can help ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 11/16/2021 09:14:16New subject after splitting |
|
11/16/2021 10:32 AM | |
Joined: 10/7/2005 Last visit: 11/19/2024 Posts: 3027 Rating: (1057)
|
I presume this PUT SFB15 is running in an S7-400, correct? If so, a CPU restart is required to activate the changed address parameters. |
Cheers |
|
This contribution was helpful to1 thankful Users |