Hi Binh, Your issue is not in the right place. You shoud put in new thread in Simovert Masterdrive conference. Anyway, why didn't you follow steps from manual? So From Version V1.30 onwards, automatic motor identification is available. In the case of non-Siemens motors (P095 = 3 or 4), the rating plate data and number of pole pairs have to be entered, and then automatic parameterizing is called with P115 = 1. After exit from the "drive initial start-up" status with P060 = 1, P115 = 2 is set and hence motor identification is selected. The converter must now be switched in within 30 s so that measuring can start. The alarm A078 is set during the 30 s. wrote: The motor shaft can move slightly during the measurement operation. The motor cables are live. Voltages are present at the converter output terminals and hence also at the motor terminals; they are therefore hazardous to touch. First input the motor data, then P115=1 and after P115=2.... More in manual mc24_kompendium (page 141) Hope this will helps. Best regards Hristo Mihalev |
6/29/2009 4:54 AM | |
Posts: 13 Rating: (0) |
Dear Sir, - Tks - Today, I wil try again |