@D Christof, My application was made in 2015 using TIA V13.0, not V13 + SP2. Now, I am trying to upgrade it to V17.0. So I opened the archive in V17.0 and the app upgraded to V17.0. Now The WinCC RT Advanced is not communicating with the PLCs simulated by PLCSim V17.0 So, Is this because the V13.0 app was not first saved in V13.2 format before upgrading? regards ------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 06/09/2023 10:47:06New subject after splitting |
|
6/15/2023 1:29 PM | |
Joined: 8/3/2009 Last visit: 11/19/2024 Posts: 14211 Rating: (1775)
|
Hello Raj Iyer Have a look at this FAQ: https://support.industry.siemens.com/cs/de/en/view/109742764 So your HMI image you use has to be >V13.0.1 or newer (perhaps your image is still V13 or smaller). So do a rightclick on the RT Advanced-> Change device/version ->Select the Adv RT in the newest Version you can choose. If this does not the job then check also the basics: https://support.industry.siemens.com/cs/de/en/view/109748099 Bye Murof |