7/10/2015 11:24 AM | |
Posts: 457 Rating: (46) |
Hello K.Jagan, Please see this link: https://support.industry.siemens.com/tf/ww/de/posts/99586/ Sorry, it's only in german language, but I think the last contribution will help you: he renamed in projectpath ...\\wincproj\OS_XXX\ all files *.dcf with another name, started project again. If it runs, you can delete these files. Georg
|
7/10/2015 11:35 AM | |
Posts: 457 Rating: (46) |
Additionlly, I found here some hints: https://support.industry.siemens.com/tf/ww/en/posts/108937/ Same user/password must be configured on all machines... Georg |
7/10/2015 12:01 PM | |
Joined: 10/3/2010 Last visit: 10/17/2024 Posts: 1562 Rating: (192) |
and make sure that Simatic Shell is good on each station.. |
B r g d s , |
|