6/9/2017 6:54 AM | |
Posts: 5 Rating: (0) |
if u do not want sent 24V in the current loop,set the module to four wire current transmitter,and you must also set in hardware config |
6/9/2017 7:53 AM | |
Joined: 5/15/2010 Last visit: 2/8/2024 Posts: 172 Rating: (3) |
Hi, This card is of universal type. Here you can select analog channel as 4 wire in order to avoid 24VDC on terminal of channel. The selection can be in properties option of that very card. You can select the wiring type on channel basis. You may refer attached wiring example. Attachments7300_module_7KF02.pdf (156 Downloads) |
Last edited by: vinit at: 6/9/2017 7:59:41 AM |
|