Hello Pawan Kumar; The question has been asked often in the forum (search for "Y-Link and SWR" for example, using the Search Box at the right of this page) and the answer always is: Siemens does not support the Y-Link for SWR. So you cannot link the single-sided Profibus slaves (such as your drive) to the redundant section of the SWR program. But you can use the non-redundant part of the program to communicate with the slave (the comms will not be redundant. See.the information provided in this link: software redundancy with y link https://support.industry.siemens.com/tf/ww/en/posts/88693/ Hope this helps, Daniel Chartier |