Hello! I am trying to change the device type from TP177A 6" to TP177B PN/DP 6". I have the original WinCC 2008 Flexible project. When I go to compile the project after changing the device type, I get 4 errors - Snip1 in the attached file. However, checking the area pointers and connections, the parameters are the same - snip 2. Any ideas? AttachmentSnips.zip (579 Downloads) |
5/27/2022 2:09 PM | |
Joined: 8/3/2009 Last visit: 11/13/2024 Posts: 14165 Rating: (1774)
|
Hello vasilevdim CHeck here the requirements for your area pointers: https://support.industry.siemens.com/cs/de/en/view/18797552/9652164363 at Date/Time you need an array of 6 words if you work with symbolic tags. If you delete the PLC Item in the area Pointer and just work with the absolute address you can also use other datatypes in the DB but WinCC flex expects 6 words. In Job mailboy you need 4 words. Bye Murof |