Hello, The quickset calibration check procedure on a DMF180 failed when reaching the pivoting check: the Z axis offset is wrong (shifted up by the length of the mounted touch probe in the spindle), so the swivel is done "in the air" from -45° to +45° instead of on the calibration ball and thus ends with an error: "no contact detected" (by the touch probe) I cannot find where is the parameter to adjust the Z axis offset needed during the swivel/pivoting The problem may come that the very first quickset procedure was ran inadvertently in mode 2 (direct rewrite) instead of mode 1 (measure + rewrite of the values) See attached video - the problem appears at the last seconds of the video: the head moves up left while swiveling.instead of staying in contact with the ball. Thank you, Attachmentquickset.MOV (321 Downloads) |
12/3/2022 6:21 PM | |
Joined: 1/24/2021 Last visit: 9/16/2024 Posts: 191 Rating: (21) |
Seems the offset vectors of kinematic table are wrong. Read attached document. Attachmentkinematic chain.pdf (385 Downloads) |