Hello, everyone. This error appeared rarely but in the last two weeks it has been appearing every 5 minutes. We have H system with two 6ES7 417-4HT14-0AB0 . How can I solve it? Thanks for your help. AttachmentDiagnose_novo.txt (590 Downloads) |
Last edited by: The Helping Hand at: 02/02/2023 08:25:11Text formatting optimized. |
|
2/7/2023 11:02 AM | |
Joined: 5/3/2017 Last visit: 5/21/2024 Posts: 673 Rating: (217) |
Hi Urai.Guerreiro, The controller of the SIMATIC product line have a basic cycle monitoring (OB1) of 6 seconds maximum. If the cycle checkpoint is not reached within 6 seconds, OB80 (time error) will be called and a system message will be issued. If the basic cycle of the OB1 is immediately exceeded once more after the first interruption, the plant goes into the condition STOP. The best way to prevent the cycle time exceed is to move program functionally from a faster OB to a slower OB, for example the temperature control from OB35 to OB32. With regards |
Last edited by: Heisenberg2 at: 02/07/2023 11:53:32 |
|
This contribution was helpful to1 thankful Users |
2/25/2023 6:04 AM | |
Joined: 1/11/2019 Last visit: 9/25/2024 Posts: 764 Rating: (150)
|
Hi, EN_MSG=0 will set all your incoming alarms of RACK to suppress. You will not be getting any alarms in OS! |
4/5/2023 12:59 PM | |
Joined: 1/7/2022 Last visit: 3/28/2024 Posts: 9 Rating: (0) |
Hi, everyone. I'm still getting those messages. I going to open a ticket. |