Hello, I have read instructions. After transfer bios to USB, restarted Simatic Field PG, pressing ESC, but it did not open program for bios update. When I press F2 I enter into bios, but there no options for bios update. Please, how to start program for bios update, or do you have program for DOS for bios upgrade. Regards
------------------------------------------------------------------------------------------ |
Last edited by: Jen_Moderator at: 9/21/2018 8:41:29 AMNew subject after splitting |
|
9/21/2018 9:41 AM | |
Joined: 10/18/2012 Last visit: 10/21/2024 Posts: 225 Rating: (23) |
Hello zivmil, You must press ESC directly after you power on your Field-PG. The option to enter BIOS-menu is visible only for a very short time. You have to be fast!!! ;-) If you missed it, and your Field-PG starts the operating system, shut the system down and try it again! Btw, once you have managed to enter the BIOS Menu, you can adjust the time the Field-PG is waiting for you to press ESC in future. To do so, enter "SCU" and go to the Menu "Boot -> Boot Delay Time" and enter a value, greater than the actual value. Press F10 to save the changed setting. A detailed description about BIOS updates for SIMATIC IPCs is here: Have fun! ;-) regards, |